Could someone explain to me why we get the readings that we do with pot lights?
Dave Oshust Level I Portage la Prairie, MB., CANADA www.ggtia.com
Missing insulation, check with moisture meter (for insurance).
ITC Level 1 certification NO. 2010RU33N088
Certified Home Inspector NACHI10090907
FLIR T640, FLIR Reporter 8.5
http://www.hexagon-build.com/
Sofia, Bulgaria (EU)
These are often a place where air leakage occurs. My bet is you are seeing air infiltration around the fixture. You can check this with a (cold) smoke pencil near the light to see if air is moving into the building. Even IC fixtures, supposedly air tight, leak.
In many cases, the insulation is moved away from the pot light due to minimum clearances, depends on light type.
marc m In many cases, the insulation is moved away from the pot light due to minimum clearances, depends on light type.
They sell cover designed just for this. This is just one manufacturer, there are several.